[TRNSYS-users] PCM in Buildings

David BRADLEY d.bradley at tess-inc.com
Mon Jun 6 08:03:58 PDT 2022


Ahmad,

  I am aware of three components for modeling PCMs. Unfortunately none 
of them are in the standard Trnsys library.


  There is a free one in TRNLib 
(https://sel.me.wisc.edu/trnsys/trnlib/library16.htm#thermalstorage). It 
was written quite some time ago and donated by the author. It will need 
to be recompiled as a 64-bit dll if it is to be used with v18 or you can 
use the 32-bit version of Trnsys18. In order to recompile, it might need 
some source code changes that would be detailed in the 07-Programmer's 
Guide manual. I don't have any direct experience with this model but 
know that it assumes the PCM to be on the outside surface of the wall 
(in contact with the zone air)


   Transsolar offers a stand-alone PCM component called Type399. You can 
see some information (including downloading the documentation) here: 
https://trnsys.de/en/addons-en. Again I don't have any direct experience 
with the model so unfortunately can't offer any advice.


   The third one is a model that I wrote some years ago and that we 
offer as a stand-alone component. I can send you technical information. 
The component listed here: 
http://trnsys.com/tess-libraries/individual-components.php.html. This 
PCM model assumes that the PCM layer is somewhere within the interior of 
the wall (i.e. not in direct contact with zone air although there are 
some ways to get around that.


   I do not know of a cool roof paint model though as a side note, part 
of the idea of Trnsys is to make it possible for users to develop and 
add their new components.


kind regards,

  David







On 06/06/2022 04:17, Dr. Ahmad Sedaghat via TRNSYS-users wrote:
> Dear friends
>
> We purchased the full TRNSYS with TESS library package few days ago. 
> However, I am keen to use PCM in wall and roofs of a building and Cool 
> Roof paint. So far, I couldn't find any useful types to do the task. I 
> wonder if you can advise us on using specific PCM types available in 
> our RNSYS license or you could kindly guide us with these Types.
>
> Many thanks in advance for your support.
> Best regards
> Ahmad
>
>
> Dr. Ahmad Sedaghat​
>
>
> Associate Professor ‑ Mechanical Engineering
> College of Engineering
> Hotline: +965 1828225 Ext: 4295
>
> www.ack.edu.kw <http://www.ack.edu.kw/>
>
> ------------------------------------------------------------------------
> *From:* Technical Support <TechSupport at tess-inc.com>
> *Sent:* Wednesday, June 1, 2022 2:29 PM
> *To:* Dr. Ahmad Sedaghat <a.sedaghat at ack.edu.kw>
> *Subject:* Re: Fw: Fwd: AU PO.12543 - Thermal Energy System 
> Specialists LLC
>
> Prof Sedaghat,
>
>  Thank you for the confirmation.
>
> kind regards,
>
>  David
>
>
> ---
>
> Technical Support Team
> Thermal Energy System Specialists, LLC
> 3 N. Pinckney St, Suite 202
> Madison, WI 53703
> techsupport at tess-inc.com
> www.tess-inc.com <http://www.tess-inc.com/>
> www.trnsys.com <http://www.trnsys.com/>
> TRNSYS on Facebook <http://www.facebook.com/TRNSYS>
>
>
>
>
> -------- Original Message --------
>
> Subject: 	Fw: Fwd: AU PO.12543 - Thermal Energy System Specialists LLC
> Date: 	2022-06-01 04:07
> From: 	"Dr. Ahmad Sedaghat" <a.sedaghat at ack.edu.kw>
> To: 	Technical Support <TechSupport at tess-inc.com>
>
>
> Hi David
> Thanks for your request. Yes, my information is correct as listed in 
> your email.
> Regards
> Ahmad Sedaghat
> Dr. Ahmad Sedaghat​
>
> Associate Professor ‑ Mechanical Engineering
> College of Engineering
> Hotline: +965 1828225 Ext: 4295
>
> www.ack.edu.kw <http://www.ack.edu.kw/>
>
> ------------------------------------------------------------------------
> *From:* Heba Kobaissi <h.kobaissi at ack.edu.kw>
> *Sent:* Wednesday, June 1, 2022 8:25 AM
> *To:* Dr. Ahmad Sedaghat <a.sedaghat at ack.edu.kw>
> *Cc:* Dr. Sayed Mohamad Soleimani <s.soleimani at ack.edu.kw>; Dr. Khalil 
> Mohamad Khanafer <k.khanafer at ack.edu.kw>
> *Subject:* FW: Fwd: AU PO.12543 - Thermal Energy System Specialists LLC
>
> Dear Dr. Sedaghat,
>
> Please refer to below email for your kind action and response.
>
> Regards,
>
> Heba Kobaissi​
>
> Senior Officer ‑ Academic Administration
> College of Engineering
> Hotline: +965 1828225 Ext: 4233
>
> www.ack.edu.kw <http://www.ack.edu.kw/>
>
> *From:* Anthony Noronha <a.noronha at ack.edu.kw>
> *Sent:* Wednesday, June 1, 2022 7:42 AM
> *To:* Heba Kobaissi <h.kobaissi at ack.edu.kw>
> *Cc:* Abdulhadi Al Sharaa <a.sharaa at ack.edu.kw>; Purchase <pur at ack.edu.kw>
> *Subject:* FW: Fwd: AU PO.12543 - Thermal Energy System Specialists LLC
>
> Dear Heba,
> Below email FYI
> Regards,
>
> *Anthony Noronha**​*
>
> Purchaser ‑ Administrative
>
> Purchasing
>
> Hotline: +965 1828225 Ext: 4019
>
> <http://www.ack.edu.kw/>
>
> -----Original Message-----
> From: Technical Support <TechSupport at tess-inc.com>
> Sent: Tuesday, May 31, 2022 8:22 PM
> To: Anthony Noronha <a.noronha at ack.edu.kw>
> Cc: Abdulhadi Al Sharaa <a.sharaa at ack.edu.kw>; Purchase <pur at ack.edu.kw>
> Subject: Re: Fwd: AU PO.12543 - Thermal Energy System Specialists LLC
>
> Anthony,
> Thank you for the purchase order; it appears to be in good order. 
> Could you please confirm or correct the following information 
> regarding the end user:
>
> Institution: Australian University - Kuwait
> Department: School of Engineering
> Primary User: Ahmad Sedaghat
> Primary User Email Address: a.sedaghat at ack.edu.kw
>
> kind regards,
> David
>
>
> ---
> Technical Support Team
> Thermal Energy System Specialists, LLC
> 3 N. Pinckney St, Suite 202
> Madison, WI 53703
> techsupport at tess-inc.com
> www.tess-inc.com <http://www.tess-inc.com>
> www.trnsys.com <http://www.trnsys.com>
> TRNSYS on Facebook
>
> -------- Original Message --------
> Subject: Fwd: AU PO.12543 - Thermal Energy System Specialists LLC
> Date: 2022-05-31 08:03
> From: tessinc at tess-inc.com
> To: techsupport at tess-inc.com
>
> -------- Original Message --------
> Subject: AU PO.12543 - Thermal Energy System Specialists LLC
> Date: 2022-05-30 22:26
> From: Anthony Noronha <a.noronha at ack.edu.kw>
> To: "tessinc at tess-inc.com" <tessinc at tess-inc.com>
> Cc: Abdulhadi Al Sharaa <a.sharaa at ack.edu.kw>, Purchase <pur at ack.edu.kw>
>
> Dear Sir,
>
> Greetings from AU!
>
> We are pleased to place the attached Purchase Order as per below
> tabulation:
>
> AU PO#
>
> Dated
>
> Supplier Quote#
>
> Dated
>
> Promised delivery / Service completion date
>
> Brief description of
>
> Goods / Service
>
> Total PO amount In KD
>
> 12543
>
> 29-May-22
>
> Proforma Inv # 3033
>
> 15-Feb-22
>
> TRNSYS Software Package
>
> USD 3,892.62
>
> Please ensure to:
>
> Ø Acknowledge the receipt of this PO by replying to this email
> (pur at au.edu.kw)
>
> With expected goods delivery OR service completion date(s) for our 
> Quality Management System purpose.
>
> Ø ONLY in case of agreed advance payment term, please submit the
> fresh-dated pre-payment Invoice (Proforma Invoice) clearly stating AU 
> PO# for processing the pre-payment.
>
> Ø Upon completion of goods delivery OR service, please submit the
> fresh-dated Invoice clearly stating AU PO# with all applicable 
> attachments / completion documents to:
>
> ACK Purchasing Dept.
>
> Building# 1, 1st floor
>
> Regular working hours: 8 am to 3:30 pm (Sunday to Thursday)
>
> Please revert to the undersigned (AU Purchasing) in case of further 
> clarifications / updates.
>
> Thanks & Best Regards,
>
> Anthony Noronha​
>
> Purchaser ‑ Administrative
>
> Purchasing
>
> Hotline: +965 1828225 Ext: 4019
>
> [1]
>
>
>
> Links:
> ------
> [1] http://www.ack.edu.kw/
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/f187b77c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image627238.png
Type: image/png
Size: 4766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/f187b77c/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image950270.png
Type: image/png
Size: 4766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/f187b77c/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image443319.png
Type: image/png
Size: 4766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/f187b77c/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image755825.png
Type: image/png
Size: 4766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/f187b77c/attachment-0007.png>


More information about the TRNSYS-users mailing list