David BRADLEY d.bradley at tess-inc.com
Mon Jun 6 06:15:18 PDT 2022


Nina,

   Make sure that the questions in the parameter, output, and derivative 
tabs of the Type4 proformas are all answered in a consistent way. 
Because of the way the questions are worded, you need to have at least 3 
nodes in your tank.

kind regards,

  David


On 06/05/2022 18:25, Nina Monteiro via TRNSYS-users wrote:
>
> Hi there,
>
> I have been getting this error message:
>
> Which somewhat makes sense, because the source code writes:
>
>     Ind = 1
>
>     uaf   = getParameterValue(17+ind)
>
>     tflue = getParameterValue(18+ind)
>
>     tboil = getParameterValue(19+ind)
>
> I am also getting:
>
> Which appears to be strange, as I checked and double-checked and I do 
> not think I did anything wrong upon inputting the node.
>
> If anyone has any idea on how to fix it, I would be very grateful.
>
> Cheers,
>
> Nina
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/d9f1f85a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 20610 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/d9f1f85a/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 22316 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220606/d9f1f85a/attachment-0003.png>


More information about the TRNSYS-users mailing list