  I am not sure I understand whether you are trying to create a 
construction that has 2 layers of heating tubes or whether you are 
trying to avoid creating such a construction. Can you please clarify 
whether the picture that you included is what you want to model or if it 
is what you are concerned might be happening?


  In general, an ADJACENT wall (or floor or ceiling) defined in TRNBuild 
does not have any mirroring in it. You create the layers of the wall 
however you wish and then you go to one of the two zones to which the 
wall is adjacent and you set whether that zone contains the front or the 
back of the wall. So if the construction you create is made up of the 
layers: sol, dale, tubes, chape, parquet and you define that 
construction to be ADJACENT (between two zones) then one of the zones 
will have the "sol" face and the other zone will have the "parquet" face 
in it.


  If, on the other hand, you want to have a construction that has two 
active layers in it you'll need to define something called a "direct 
contact" zone in between them. This is a kind of very low volume virtual 
airnode that sits between two BOUNDARY constructions. Defining one can 
be confusing so if the picture below represents what you want, please 
let me know and I'll try to explain how to do it.


  Two side notes:


1. the picture you sent seems like it is intended for a ground floor 
rather than for an adjacent floor (given the compacted soil layer). If 
that is indeed the case then you'll want to define the construction as a 
BOUNDARY rather than as ADJACENT.

2. you're going to need to sandwich the tubing layer between two screed 
(chape) layers. When you are defining the construction enter the first 
screed layer as having half of the actual layer's thickness. Next add 
the active layer and a second screed layer will be added below it. You 
can move the tubing layer up and down in the screed layer by adjusting 
the thickensses of the two adjoining layers but you can't put the tubing 
at the very bottom of the screed layer as it is pictured in your drawing.


kind regards,

  David



On 06/01/2022 14:48, Said LAMGHARI wrote:
> Dear David;
> The creation of a floor or wall is done from the inside to the outside.
> When I change the construction type of two adjacency room.
> I notice that it applies to the wall or the ceiling of the other room. 
> I noticed that it is the mirror effect on the adjacency walls.
> The attached figure shows my idea that I have on the floor study. 
> please confirm this to me,  if I m right or not.
> Best.
> Said LAMGHARI
>
>
> ------------------------------------------------------------------------
> *De :* David BRADLEY <d.bradley at tess-inc.com>
> *Envoyé :* mercredi 1 juin 2022 15:23
> *À :* TRNSYS users mailing list at OneBuilding.org 
> <trnsys-users at lists.onebuilding.org>
> *Cc :* Said LAMGHARI <said.lamghari at edu.uca.ma>
> *Objet :* Re: [TRNSYS-users] Underfloor heating
>
> Said,
>
>  Trnsys tries to mimic what would happen in a real world situation; if 
> you put an active layer into a floor that is also the ceiling of 
> another zone and put hot water through it then the floor/ceiling will 
> heat both the zone above and the zone below. To prevent that from 
> happening, you can put insulation on the side that you do not want to 
> be heated.
>
> kind regards,
>
>  David
>
>
>
>
> On 06/01/2022 04:35, Said LAMGHARI via TRNSYS-users wrote:
>> Dear All,
>> I have a question about underfloor heating.
>> Between the floor and the ceiling of two adjacent rooms (ADJ_ceiling) 
>> . Do you have any idea about underfloor heating. since we will have 
>> the mirror effect on this floor so we will have two active layers..! 
>> or not!
>> Best,
>> Said LAMGHARI
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org  <mailto:TRNSYS-users at lists.onebuilding.org>
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org  <http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy System Specialists, LLC
> 3 North Pinckney Street - suite 202
> Madison, WI  53703 USA
>
> P:+1.608.274.2577
> d.bradley at tess-inc.com  <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com  <http://www.tess-inc.com>
> http://www.trnsys.com  <http://www.trnsys.com>

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220602/1aa42fb4/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: plancher.png
Type: image/png
Size: 125633 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220602/1aa42fb4/attachment-0001.png>


More information about the TRNSYS-users mailing list