On 2022-01-21 10:50, Zhyan Faeaq via TRNSYS-users wrote:
> I have (10) panels of flat plate solar collectors arranged in (2) rows
> (5 by 5) parallel to each other, and each of (2m^2 ) in area, and I
> use type (1b) . My question is:
> 1. If I want to add the number in series in the parameter section
> which number shall I add (Ten or Five), also about the collector area,
> shall I add total area or just area of the series collectors?
> 2. About the inlet flow in the inputs section should I add the total
> flow-rate or just this flow-rate enters the series collectors? means
> the half flow-rate
This has been covered many times on this forum but I'll save you some
time looking through the archives:
1) 5 in series if I understand your design. The number of panels that
one molecule of water flows through each pass.
2) Specify the total area of all the modules
3) Specify the total flow rate to the array
4) Consider upgrading Type 1 to one of the new solar collectors from the
TESS Libraries - it makes specifying this information easier and has
added control options and the ability to include the impact of the mass.
Jeff
--