Use a heating aquastat with a setpoint of 76 and a deadband of 12 C. Then use an equation connected to your aquastat to set the boiler input:
f_Boiler = 0.75 + 0.25 * y_Aquastat
Jeff
Sent from my iPhone
> On Apr 6, 2022, at 9:56 AM, Böttner, Jan via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
> Hey,
>
> I have difficulties getting my code correct.
> I want to reduce the power of my boiler at 82°C to 75% but don’t want it to go up to 100% right away when the Temperature drops below 82°C but rather at 70°C.
> But i don’t seem to find the right place in the code to make this happen.
>
> Any ideas on this?
>
> Thanks!
> Jan