[TRNSYS-users] Possible bug with type919 water source heat pump
David BRADLEY
d.bradley at tess-inc.com
Thu Sep 16 10:35:39 PDT 2021
Jim,
The quick fix is that you can set the units of the fraction of
outside air to "variable name" (or "string" if you're using v17) and
then define and use an equation that sets the fraction of outside air
rather than keying in a value.
The more rigorous fix is the following:
- open the Type919 proforma from within the Simulation Studio.
- switch to the "variables" tab, click on the "variables" button and
then filter on "inputs"
- find the "fraction of outside air" input and click the "modify" button.
- make sure that the "type" field is set to "real" and not "integer"
- save the change in the proforma, close it and then drag a new one out
into your project. Check to make sure that you can set the value to
anything between 0 and 1
Once you have verified that the fix works, you'll need to right click on
the instance(s) of Type919 in your project and select "replace" from the
context menu.
kind regards,
David
On 09/16/2021 10:03, dimitris soukoulis via TRNSYS-users wrote:
>
> Dear All,
>
> While trying to change the input #20: Fraction of outside air, from
> the type919 Water source heat pump, I realized that the only possible
> values it accepts are 0 and 1. Everything in between will not work. Is
> there a simple fix for that problem, or is it a coding problem?
>
> Kind regards,
>
> Jim Soukoulis
>
> NTUA
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210916/76d81d7a/attachment.html>
More information about the TRNSYS-users
mailing list