[TRNSYS-users] Type 1716b Rotary Desiccant Dehumidifier - Known Regeneration Temperature
David BRADLEY
d.bradley at tess-inc.com
Mon Oct 18 08:54:59 PDT 2021
Habiba Aly,
The regeneration air inlet temperature is the temperature at which
regeneration air enters the dehumidifier before it is heated to its
known regeneration temperature. The "regeneration temperature" input is
the known regeneration temperature.
For future reference, clicking on the "more" button next to a
parameter, input, or output can give you a bit more information about a
particular value that the model either needs or computes.
kind regards,
David
On 10/18/2021 07:17, Habiba Aly via TRNSYS-users wrote:
> Hello Trnsys users,
>
> What is the difference between regeneration air inlet temperature and
> regeneration temperature in type 1716b inputs. i have the dehumidifier
> coupled with heating coil and fan components so that air temperature
> at dehumidifier inlet is regeneration temperature, is that wrong? Does
> the humidifier component already have a heating element within?
> attached is my configuration picture.
>
> Thank you,
> Habiba Aly
> image.png
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211018/c7d3487e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 5688 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211018/c7d3487e/attachment-0002.png>
More information about the TRNSYS-users
mailing list