[TRNSYS-users] Type519a
吉永 美香
yoshi at meijo-u.ac.jp
Fri May 21 17:31:41 PDT 2021
Hi, Yoon-sensei,
I tried to use Type519 and found all the same error you said. I
suppose that the Japanese code like Shift-JIS in our PCs may cause the
problem.
Scheduler.exe connected with Type519 uses Microsoft Outlook formatted
file (*.hol) and it seems to make the error. MultSched.exe working
with Type516 doesn't use Outlook file and makes no problem.
unfortunately, this kinds of trouble is very familiar to me. you
should avoid to use Type519 or tried to use other PC with
English-based OS at the moment.
needless to say, if TESS can change using Scheduler.exe in Type519 to
MultSched.exe is the most desirable solution. thank you, David!
Best regard,
Mika
==============================
Mika Yoshinaga
Professor, Meijo University
Shiogamaguchi1-501,Tempaku, Nagoya
Email: yoshi at meijo-u.ac.jp
==============================
2021年5月22日(土) 8:13 Gyuyoung Yoon via TRNSYS-users
<trnsys-users at lists.onebuilding.org>:
>
> Dear David,
>
> Thank you for your email. I tried to reinstall the TESS library but it could not fix the problem.
> On the other hand, I can use the Type 516, 518 without any trouble, so it seems to be a problem on the Type 519 only.
>
> Best regards
> ------------------------------------------------------
> Gyuyoung YOON, Dr. Eng.
> Associate Prof., Nagoya City University
> Tel/Fax +81-52-721-3175
> Skype ID : yoon.gyuyoung
> yoon at yoonlab.net
> yoon at sda.nagoya-cu.ac.jp
> http://www.yoonlab.net
> ------------------------------------------------------
>
>
> On Fri, May 21, 2021 at 11:29 PM David BRADLEY <d.bradley at tess-inc.com> wrote:
>>
>> Prof Yoon,
>>
>> I have had this happen a few times and have never found a very elegant solution other than reinstalling the TESS Libraries. I think the problem has to do with some system files used by the plugin that get coopted by other system resources. Reinstalling seems to reassociate those files with the plugin again.
>>
>> kind regards,
>>
>> David
>>
>>
>> On 05/20/2021 22:22, Gyuyoung Yoon via TRNSYS-users wrote:
>>
>> Dear All,
>>
>> I am having trouble using Type 519a.
>> Scheduler shows me the message of " Rum-time error '13': Type mismatch"
>>
>> I have confirmed the path for the external file of **.hol (the sample one), there is no problem.
>> It seems that the **.hol file can be read at the first time when the "Schedule Set-Up" window open,
>>
>> Would anybody tell me what the problem is?
>> ------------------------------------------------------
>> Gyuyoung YOON, Dr. Eng.
>> Associate Prof., Nagoya City University
>> Tel/Fax +81-52-721-3175
>> Skype ID : yoon.gyuyoung
>> yoon at yoonlab.net
>> yoon at sda.nagoya-cu.ac.jp
>> http://www.yoonlab.net
>> ------------------------------------------------------
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>> --
>> ***************************
>> David BRADLEY
>> Principal
>> Thermal Energy Systems Specialists, LLC
>> 3 North Pinckney Street - suite 202
>> Madison, WI 53703 USA
>>
>> P:+1.608.274.2577
>> d.bradley at tess-inc.com
>>
>> http://www.tess-inc.com
>> http://www.trnsys.com
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
More information about the TRNSYS-users
mailing list