Changing the units of an input in a proforma does not create an 
automatic conversion. The model requires that the flow rate inputs be 
given in kg/h. If your upstream component is outputting a flowrate it 
kg/s then you will need to put an equation in between it and the Type534 
in order to manually convert the value.

kind regards,

  David


On 06/26/2021 01:47, Maryam Khademi via TRNSYS-users wrote:
>
> Hi guys,
>
> How I can define variable flow rate for storage tank ports of type 534?
>
> And I defined flow rates of tanks in kg per second but surprisingly 
> when I plot these flow rates, are multiplied by 1000.
>
> I cannot find what is the reason!!!
>
> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for 
> Windows 10
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************