[TRNSYS-users] Question about selecting boundary temperatures in TRNBUILD
Marion Hiller
Hiller at Transsolar.com
Fri Jun 18 00:13:56 PDT 2021
Hi Amin,
the main difference is that for “Identical” the same absorbed solar radiation and longwave radiation gains are imposed on the back side of the surfaces in addition to convective heat transfere.
“Userdefined” doesn’t include any radiation gain. Only a heat transfer from the surface node defined by the “convective heat transfer coefficient” of the back sides of the surface and the given temperature is calculated.
More detailed information is given int eh Type56 manual.
Regards,
Marion
Transsolar Software Team
hotline at transsolar.com
Transsolar
Stuttgart | Munich | Paris | New York
Transsolar Energietechnik GmbH | Curiestrasse 2 | 70563 Stuttgart | Germany
CEO: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag von Amin HADDAD via TRNSYS-users
Gesendet: Mittwoch, 16. Juni 2021 13:50
An: TRNSYS users mailing list at OneBuilding.org <TRNSYS-users at lists.onebuilding.org>
Cc: Amin HADDAD <itshaddad1 at gmail.com>
Betreff: [TRNSYS-users] Question about selecting boundary temperatures in TRNBUILD
Hi dear users,
I would like to know, when selecting a boundary wall, how TRNBUILD (Type 56) will assume or calculate the temperature boundary condition when choosing the option "Identical" instead of selecting ''Userdefined'' ?
Thank you for helping
Regards
Amin
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210618/2b628dc0/attachment.htm>
More information about the TRNSYS-users
mailing list