Use a Type 14 forcing function to set the time window in which the tank is allowed to be heated. Then use an equation and multiply the output of the forcing function by the output of the controller and feed that result to the heating element.
Jeff / TESS
> On Jun 3, 2021, at 1:38 PM, Janus Rathke via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
> Hi all
>
> Hope you are well!
>
> I am trying to configure a setup of a water tank, which will be heated to 30 degrees, two times a day, 1 time at 9 am and then again at 9pm.
> However i tried to play with the controllers, but none of them seems to allow periodically heating of water tanks.
>
> Can anybody help with this?
>