[TRNSYS-users] Convergence problem for the internal regulation
David BRADLEY
d.bradley at tess-inc.com
Thu Jan 7 08:27:31 PST 2021
Hugo,
This kind of problem is not uncommon, especially when doing combined
airflow/thermal simulations. I have not run into the problem of
convergence problems inside of Type56, which is a little surprising. I
thought that I had gotten all of the possible TRNSYS errors at least
once! The solution I usually use is to implement a short time step (1
minute perhaps) and then to put a delay component (like Type661 or
Type150) between Type56's output temperatures and Type98's inputs. It is
a bit of a cheat but I think with a short timestep it is realistic
enough. We assume that air entering a Type56 zone immediately mixes
thermally with the zone air and that thermostats react immediately. When
you add the automatic heating/cooling that Type56 can do you are further
assuming that the mechanical systems can react instantaneously and
provide exactly the right amount of heating and cooling. I don't think
it is unreasonable to introduce back a small time delay in order to get
the whole thing to converge.
kind regards,
David
On 01/07/2021 09:05, Hugo GEOFFROY via TRNSYS-users wrote:
>
> Hello,
>
> We need to modelize a few stories building in a cosimulation
> TRNSYS/CONTAM.
>
> The thermal part is handled by TRNSYS with a Type 56 and the aeraulic
> part by CONTAM with a Type 98.
>
> The model works but encounters several convergence problems as noticed
> in the *.lst file. The model includes daily windows openings that
> coincide with the convergence problem occurrences. Furthermore, most
> of the rooms are heated with an ideal system of which power is limited
> to 100 W.m-2. The setpoint temperature is fixed thanks to a schedule
> in the "Heating type manager"
>
> Removing this heating resolves the convergence problem, but these
> convergence faults cannot be fixed by reducing the time step,
> modifying the number of iterations, or convergence tolerance of
> Simulation Studio. The following error message shows that the faults
> are not directly generated in the "simulation studio" calculation but
> by Type 56 and are indeed a consequence of the heating of the building
> Type 56 model.
>
> --------------------------------------------------------
>
> *** Notice at time : 130.000000
>
> Generated by Unit : 56
>
> Generated by Type : 56
>
> Message : TIME = 130.000 More than 6
> iterations for internal regulation HEATING/COOLING
>
> *** Warning at time : 130.000000
>
> Generated by Unit : 56
>
> Generated by Type : 56
>
> Message : TIME = 130.000 CONVERGENCE NOT
> ATTAINED USING INTERNAL REGULATION FOR HEATING/COOLING
>
> -------------------------------------------------------
>
> This fault appears while the *.dck maximal iteration is fixed to 500.
>
> Has somebody already encountered this problem in Simulation studio ?
>
> Is it possible and if yes, how the numerical parameters (tolerance of
> convergence, number of iterations, …) of Type56 can be modified? Do
> you have any idea for another solution to solve this problem?
>
> Thank you
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210107/21622cbd/attachment-0001.html>
More information about the TRNSYS-users
mailing list