I often use QIBAB and QIDAB (NTypes 80 and 81). Those are the
quantities of radiation absorbed (as opposed to incident) on the inside
surface, however.
Wall gains are specified as totals, not per square metre.
kind regards,
David
On 04/09/2021 05:15, K.R. Gunawardena via TRNSYS-users wrote:
>
> Hi,
>
> I am trying to get clarification on a couple of issues.
>
> I am trying to couple a bespoke component with Type 56 to calculate
> surface evaporative flux. I want to input the net radiation received
> on a specific internal surface as an input to this component. Which
> trnsys output best represents the net radiation energy received by an
> internal surface?
>
> Second, when specifying a wall gain, do we provide the value for the
> entire wall or m^2?
>
> Answers are greatly appreciated,
>
> Best regards,
>
> Kan
>
>