[TRNSYS-users] Not able to put custom input in Type 56 (Multi zone Building)
David BRADLEY
d.bradley at tess-inc.com
Thu Oct 8 06:49:58 PDT 2020
The way to do this is to make a different *.bui file for each iteration
of the parametric table then add a series of ASSIGN statements in your
*.dck so that each of the *.bui files is assigned a unique logical unit
number. You then create an equation that sets the value of the logical
unit number that Type56 will use and you replace Type56's logical unit
parameter with the name of the defined variable. When you create the
parametric table in TRNEdit, you'll select that same variable name and
assign one table run to each of the logical unit values.
kind regards,
David
On 10/08/2020 07:46, Assile Al-Jardali via TRNSYS-users wrote:
>
> Dear All;
>
> As I am conducting a parametric study for glass U-value and insulation
> thickness, please I need to know how can I make these 2 parameters and
> Input values or constants so I can use them later on in the study on
> TrnEdit.
>
> Thank you,
>
> ------------------------------------------
>
> Assile Al Jardali, MEng
>
> Mechanical Engineer
>
> Mobile:+961 70 860339
>
> E-mail: assile.aljardali at live.com
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20201008/6213f133/attachment.htm>
More information about the TRNSYS-users
mailing list