[TRNSYS-users] Surface Loss Coefficients Type 533 Horizontal Cylinder Tank
David BRADLEY
d.bradley at tess-inc.com
Thu Nov 5 07:44:11 PST 2020
Julien,
Changing parameters to inputs requires that you modify the source
code of the Type and recompile it into a new DLL. The source code for
Type533 is in the .\Tess Models\SourceCode\ directory and TRNSYSv18 has
a Fortran compiler built into it so in theory you should be able to use
the TypeStudio to make the changes that you need. I say "in theory"
because Type533 is a fairly complicated piece of code and it may not be
a trivial process to modify and recompile.
kind regards,
David
On 11/05/2020 09:17, Julien Gambade via TRNSYS-users wrote:
> Hello,
>
> I am using Type 533 Horizontal Cylinder Tank from Tess Library. I
> would like to define Surface Loss Coefficients as inputs instead of a
> parameters.
> I can't assign a variable name and I would prefer to avoid modifying
> the source code.
>
> Does anyone know a solution ?
>
> Thank you in advance,
>
> Best regards
> --
> *Julien GAMBADE*
> *Doctorant*
> Institut de Recherche Dupuy de Lôme (UMR CNRS 6027)
> Centre de recherche Christian Huygens
> Rue de Saint-Maudé - 56100 Lorient - France
> julien.gambade at univ-ubs.fr
> www.irdl.fr <http://www.irdl.fr>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20201105/02440a03/attachment.htm>
More information about the TRNSYS-users
mailing list