[TRNSYS-users] Dehumidification and natural ventilation

David BRADLEY d.bradley at tess-inc.com
Sat Mar 14 11:35:25 PDT 2020


Audun,

  There is a component called Type42 in the standard library that is 
designed to read a generic performance map. If you have performance data 
for the dehumidifier that you want to use (capacity and COP as a 
function of indoor drybulb and RH for instance) then you can use Type42 
to read and interpolate it. You would probably have to also one or more 
Type33 psychrometrics components for determine all the conditions of the 
outlet air.

kind regards,

  David


On 03/14/2020 03:06, Audun Bull Kristiansen wrote:
>
> Thanks for the good advice, David! I implemented Type 168. My 
> university only purchased /High Temp. Solar Component Library/ and 
> /Cogeneration Component Library / from the  TESS Component Libraries, 
> it seems. I guess I will have to ask them if they can purchase /HVAC 
> Component Library/ if I shall include dehumidification, or is there 
> any other component from TRNSYS 18 or the TESS libraries I mentioned 
> that we already have that I can use for this simple building?
>
> Audun
>
> *Fra: *David BRADLEY <mailto:d.bradley at tess-inc.com>
> *Sendt: *Friday, March 13, 2020 kl. 11:22 PM
> *Til: *TRNSYS users mailing list at OneBuilding.org 
> <mailto:trnsys-users at lists.onebuilding.org>
> *Kopi: *Audun Bull Kristiansen <mailto:audun.bull at hotmail.com>
> *Emne: *Re: [TRNSYS-users] Dehumidification and natural ventilation
>
> Audun.
>
> 1.  There are a number of dehumidifier models available in the TESS 
> HVAC library.
>
> 2. and 3. Since you are dealing with a relatively simple shape of 
> building, you might look at Type168 (if you are using Trnsys18). That 
> model is a good bit simpler to implement than either TRNFlow or 
> CONTAM. If it is too simplistic then it might at least give you an 
> idea as to whether natural ventilation is feasible. If it is, then you 
> could move on to one of the more complex tools. My preference is for 
> CONTAM but that is really only because I started out using CONTAM and 
> so am more familiar with it. One reason to use TRNFlow, though, would 
> be that you can define CO2 as a "contaminant" in TRNFlow and track its 
> concentration level.
>
> kind regards,
>
>  David
>
> On 03/13/2020 04:49, Audun Bull Kristiansen via TRNSYS-users wrote:
>
>     I have three questions:
>
>      1. Is it possible to model a dehumidifier (stand-alone room unit
>         as in the attached picture) in TRNSYS? I model a tiny home
>         made from a single shipping container with an air-to-air heat
>         pump (Type 119c). During the summer I lower the temperature to
>         dehumidify the air, but when there isn’t any cooling need in
>         the room it would be good to have an option to dehumidify the
>         air without cooling the entire room.
>      2. The container has a glass door and two windows, so it is a
>         good potential to use natural ventilation for cooling part of
>         the year. Can you give me some recommendation on how to model
>         this when my main goal is to study changes in indoor
>         temperature and cooling load? I have TRNFlow. I also see that
>         some researchers use a co-simulation with CONTAM Type 97 or
>         Type 98. For now I modelled it as another ventilation
>         component with zero SFP in Type 56 with an input that is based
>         on time, indoor temperature and ambient temperature from a
>         calculator.
>      3. It would also be nice to have a report of the CO2
>         concentration in the room, to see if the ventilation is
>         sufficient. But I can not see that I can select that as output
>         in TRNSYS?
>
>     Kind regards Audun
>
>     Ph.D. student at Shanghai Jiao Tong University
>
>
>
>     _______________________________________________
>
>     TRNSYS-users mailing list
>
>     TRNSYS-users at lists.onebuilding.org  <mailto:TRNSYS-users at lists.onebuilding.org>
>
>     http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 3 North Pinckney Street - suite 202
> Madison, WI  53703 USA
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com  <mailto:d.bradley at tess-inc.com>
> http://www.tess-inc.com
> http://www.trnsys.com
>
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200314/4a1c1ed2/attachment.htm>


More information about the TRNSYS-users mailing list