[TRNSYS-users] Type 557 / double-u tube
David BRADLEY
d.bradley at tess-inc.com
Mon Mar 9 12:52:26 PDT 2020
Hoofar,
The 11th parameter of Type557a (GHP Library: Ground Heat Exchangers:
Vertical: U-Tube: Standard: ) asks you to specify the number of u-tubes
per bore.
kind regards,
David
On 03/09/2020 07:09, Hemmatabady, Hoofar via TRNSYS-users wrote:
>
> Hello everyone,
>
>
> I have a question regarding type 557 in TRNSYS. There are mainly two
> type (U-tube & Tube-in-tube). How can a _2U-tube_ ground heat
> exchanger be modelled? Should I change some parameters of the single
> U-tube one?
>
> Is there probably a more user-friendly mathematical reference for type
> 557 other than type557-DST manual (I mean overview and mathematical
> reference like other TRNSYS components)?
>
>
> Best regards,
>
> Hoofar Hemmatabady
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200309/2ef873e4/attachment.htm>
More information about the TRNSYS-users
mailing list