David BRADLEY
d.bradley at tess-inc.com
Mon Mar 9 12:52:26 PDT 2020
Hoofar,
The 11th parameter of Type557a (GHP Library: Ground Heat Exchangers:
Vertical: U-Tube: Standard: ) asks you to specify the number of u-tubes
per bore.
kind regards,
David
On 03/09/2020 07:09, Hemmatabady, Hoofar via TRNSYS-users wrote:
>
> Hello everyone,
>
>
> I have a question regarding type 557 in TRNSYS. There are mainly two
> type (U-tube & Tube-in-tube). How can a _2U-tube_ ground heat
> exchanger be modelled? Should I change some parameters of the single
> U-tube one?
>
> Is there probably a more user-friendly mathematical reference for type
> 557 other than type557-DST manual (I mean overview and mathematical
> reference like other TRNSYS components)?
>
>