[TRNSYS-users] Ynt: Type 48c pv-wind system
Duygu Kemeriz
dkemeriz89 at hotmail.com
Tue Jun 23 08:47:01 PDT 2020
Hi David;
Thank you for your reply. Thats true the system is not connected to the grid. How do I change the system until the value is 0? What should I change? Could you please give an example ?
Kind Regards.
________________________________
Duygu,
If you are looking at Type48's output 5 then that value can be interpreted as "power required by the system that wasn't provided." In a grid connected system, that power would come from the grid. In a system that is not connected to the grid then you'll need to modify the system until that value goes to zero.
kind regards,
David
On 06/23/2020 09:09, Duygu Kemeriz via TRNSYS-users wrote:
Hi Trnsys users;
I have designed stand-alone solar-wind system but i have a problem about inverter is called Type 48c. My system is not connected to the grid, but when I print it from the inverter via Type 25e, it seems that there is a load coming from the grid. I want to disconnect from the grid.How can I do this or does the power from the inverter have another meaning? Do you have any ideas ?
Kind Regards
Duygu Kemeriz
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com