[TRNSYS-users] Why type11d changes the outlet temperature?
Arian Bahrami
arianbhm at yahoo.com
Sat Jun 6 13:05:49 PDT 2020
Dear Hooman
Since the temperature is constant, definitely there is no flow into the system. Your connection to the valves are somehow wrong. Check the connections.
Arian
Sent from Yahoo Mail for iPhone
On Saturday, June 6, 2020, 10:11 PM, Hooman Azad via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
#yiv3416417573 #yiv3416417573 -- _filtered {} _filtered {} _filtered {}#yiv3416417573 #yiv3416417573 p.yiv3416417573MsoNormal, #yiv3416417573 li.yiv3416417573MsoNormal, #yiv3416417573 div.yiv3416417573MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:New serif;}#yiv3416417573 a:link, #yiv3416417573 span.yiv3416417573MsoHyperlink {color:blue;text-decoration:underline;}#yiv3416417573 a:visited, #yiv3416417573 span.yiv3416417573MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv3416417573 p.yiv3416417573msonormal0, #yiv3416417573 li.yiv3416417573msonormal0, #yiv3416417573 div.yiv3416417573msonormal0 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573yahoo-quoted-begin, #yiv3416417573 li.yiv3416417573yahoo-quoted-begin, #yiv3416417573 div.yiv3416417573yahoo-quoted-begin {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msonormal0, #yiv3416417573 li.yiv3416417573msonormal0, #yiv3416417573 div.yiv3416417573msonormal0 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573yahoo-quoted-begin, #yiv3416417573 li.yiv3416417573yahoo-quoted-begin, #yiv3416417573 div.yiv3416417573yahoo-quoted-begin {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msonormal, #yiv3416417573 li.yiv3416417573msonormal, #yiv3416417573 div.yiv3416417573msonormal {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msochpdefault, #yiv3416417573 li.yiv3416417573msochpdefault, #yiv3416417573 div.yiv3416417573msochpdefault {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msonormal1, #yiv3416417573 li.yiv3416417573msonormal1, #yiv3416417573 div.yiv3416417573msonormal1 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msochpdefault1, #yiv3416417573 li.yiv3416417573msochpdefault1, #yiv3416417573 div.yiv3416417573msochpdefault1 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:New serif;}#yiv3416417573 p.yiv3416417573msonormal2, #yiv3416417573 li.yiv3416417573msonormal2, #yiv3416417573 div.yiv3416417573msonormal2 {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:serif;}#yiv3416417573 p.yiv3416417573msonormal01, #yiv3416417573 li.yiv3416417573msonormal01, #yiv3416417573 div.yiv3416417573msonormal01 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:serif;}#yiv3416417573 p.yiv3416417573yahoo-quoted-begin1, #yiv3416417573 li.yiv3416417573yahoo-quoted-begin1, #yiv3416417573 div.yiv3416417573yahoo-quoted-begin1 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:serif;}#yiv3416417573 p.yiv3416417573msonormal3, #yiv3416417573 li.yiv3416417573msonormal3, #yiv3416417573 div.yiv3416417573msonormal3 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:serif;}#yiv3416417573 p.yiv3416417573msochpdefault2, #yiv3416417573 li.yiv3416417573msochpdefault2, #yiv3416417573 div.yiv3416417573msochpdefault2 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:serif;}#yiv3416417573 p.yiv3416417573msonormal11, #yiv3416417573 li.yiv3416417573msonormal11, #yiv3416417573 div.yiv3416417573msonormal11 {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:sans-serif;}#yiv3416417573 p.yiv3416417573msochpdefault11, #yiv3416417573 li.yiv3416417573msochpdefault11, #yiv3416417573 div.yiv3416417573msochpdefault11 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:sans-serif;}#yiv3416417573 span.yiv3416417573msohyperlink {}#yiv3416417573 span.yiv3416417573msohyperlinkfollowed {}#yiv3416417573 span.yiv3416417573msohyperlink1 {}#yiv3416417573 span.yiv3416417573msohyperlinkfollowed1 {}#yiv3416417573 span.yiv3416417573emailstyle171 {}#yiv3416417573 span.yiv3416417573emailstyle30 {}#yiv3416417573 span.yiv3416417573msohyperlink2 {color:blue;text-decoration:underline;}#yiv3416417573 span.yiv3416417573msohyperlinkfollowed2 {color:purple;text-decoration:underline;}#yiv3416417573 span.yiv3416417573msohyperlink11 {color:#0563C1;text-decoration:underline;}#yiv3416417573 span.yiv3416417573msohyperlinkfollowed11 {color:#954F72;text-decoration:underline;}#yiv3416417573 span.yiv3416417573emailstyle1711 {font-family:sans-serif;color:windowtext;}#yiv3416417573 span.yiv3416417573emailstyle301 {font-family:sans-serif;color:#1F497D;}#yiv3416417573 span.yiv3416417573EmailStyle44 {font-family:sans-serif;color:#1F497D;}#yiv3416417573 .yiv3416417573MsoChpDefault {font-size:10.0pt;} _filtered {}#yiv3416417573 div.yiv3416417573WordSection1 {}#yiv3416417573
Dear Arian
You are referring to cavitation? I expect no pressure drop in the valve. Does it consider such things? Even if so, what it has to do with the temperature? Can you help me to resolve the problem?
Many thanks
Hooman
From: Arian Bahrami [mailto:arianbhm at yahoo.com]
Sent: Saturday, June 6, 2020 3:30 PM
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: Hooman Azad <hooman_azad79 at yahoo.co.uk>
Subject: Re: [TRNSYS-users] Why type11d changes the outlet temperature?
Dear Hooman,
Probably, a bubble has been trapped in the mixer valve which TRNSYS considers it in the simulation As you know, it is a powerful tool for the users.
Arian
Sent from Yahoo Mail for iPhone
On Saturday, June 6, 2020, 2:44 PM, Hooman Azad via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
Dear Arian
I wonder why while the collector outlet temperature (Mixer inlet temperature) is significantly changing, the mixer outlet temperature is fixed all the time. Do you have any idea?
Thank
Hooman
From: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] On Behalf Of Arian Bahrami via TRNSYS-users
Sent: Saturday, June 6, 2020 3:11 PM
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: Arian Bahrami <arianbhm at yahoo.com>
Subject: Re: [TRNSYS-users] Why type11d changes the outlet temperature?
Dear Hooman,
I am really sorry that nobody has responded to you. As David says always since they don’t have enough resources they can not help you about the basics.
Best Regards,
Arian
Sent from Yahoo Mail for iPhone
On Friday, June 5, 2020, 12:12 PM, Arian Bahrami via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
Hello, Hooman.
It seems you are using 16 version. Not sure if it is a bug there or not.
Arian
Sent from Yahoo Mail for iPhone
On Friday, June 5, 2020, 12:10 PM, Hooman Azad via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
Dear friends
In Figure 1 the outlets of two collectors (CPC 1 and CPC 2) with the same temperatures are connected to a type11d (Mixer). Although type11d is not supposed to change the temperatures, the mixer’s outlet temperature in Figure 2 is something fixed, not equal to inlet temperatures…. I wonder why.
Thanks for your help
Hooman
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org