[TRNSYS-users] Air-Water Heat Pump (Type 941) doesn't converge
Jeff Thornton
thornton at tess-inc.com
Tue Jul 7 10:40:37 PDT 2020
Adrian,
Any flow convergence issues you are having is likely due to something
beyond the AWHP. This type does not set the water flow rate - it simply
passes it through the device; heating or cooling it of the device is on
or simply just passing it through if the device is off. Pumps are the
devices in TRNSYS that typically set the flow rates for your loops. I
would suggest you use the TRACE feature and watch to see what is
happening when you are getting convergence issues.
Jeff
---
Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 07/05/2020 7:36 pm, Adrian Riebel Brummer via TRNSYS-users wrote:
> Dear TRNSYS users,
>
> I have a problem with Type 941 (Air-Water Heat Pump). My problem is that the simulation doesn't converge when the waterflow in the heat pump is zero, despite the heat pump is also in off mode (heating and cooling control signals are both set to zero).
>
> I have read the mathematical reference of this Type and it says something about a "Fan control signal", which functions, as I understand, as the master on-off switch of the heat pump. The problem is that I can't find that Input in the TRNSYS programm.
>
> I would like to know why I can't find that Input, and why the model doesn't converge despite the heat pump shouldn't be doing anything.
>
> I send you a picture of all the inputs that I can see for this Type. I have TRNSYS18 and TessLibs17.
>
> Regards,
>
> Adrian Riebel
>
> [2]
> Libre de virus. www.avast.com [2]
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
[2]
https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200707/7a3d86d7/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 31128 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200707/7a3d86d7/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200707/7a3d86d7/attachment-0001.gif>
More information about the TRNSYS-users
mailing list