[TRNSYS-users] Problem with Type 60
Jeff Thornton
thornton at tess-inc.com
Wed Apr 29 07:29:32 PDT 2020
May Kamal Salah,
Did you set a flow rate through the storage as well as the temperature? Type 60 is unique in that you have to specify outlet flows for (inlet flows - 1) ports. For this reason, and several other compelling reasons, we have moved away from using Type 60 and have moved this type into the archives. Most users use Type 4 in the standard library or Type 534 from the TESS Libraries. 534 is an excellent tank model and was recently coded into Energy+ as it’s faster, more accurate, and more flexible then their current tank model.
Jeff
> On Apr 29, 2020, at 3:01 AM, may kamal salah via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
> Hello Mr/Mrs,
>
> I have a problem with type 60 in Trnsys. I want to simulate a stratified tank that it´s outlet temperature varies from 8-10 degrees. I have set 10 nodes inside the tank and the inlet temperature of the tank is 18,9 C. There is no variation of the temperature even though i have set as initial temperature of the bottom of the tank 8C.
>
> thanks
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
More information about the TRNSYS-users
mailing list