[TRNSYS-users] Calculating the PMV and PPD Index with TRNSYS

David BRADLEY d.bradley at tess-inc.com
Fri Apr 3 14:08:23 PDT 2020


If they are outputs of Type56 then you will need to connect them to 
either an online plotter or to a printer component such as Type46. If 
you don't see them in the list of Type56 outputs then right click on the 
Type56 icon and select "update building variable list" from the context 
menu.

kind regards

  David


On 04/03/2020 15:59, Alexander Schneider via TRNSYS-users wrote:
> I understand, thank you very much for your help. It helped me already 
> a lot.
> But I have still a question. After I defined the outputs, where do I 
> see the results for the PMV and PPD? When I run the simulation at the 
> simulation studio it doesn’t show me any results with PMV and PPD.
>
> Hope you can help me in this case.
>
> Best regards
> Alexander
>
>> Am 03.04.2020 um 18:16 schrieb Bharat Chhugani via TRNSYS-users 
>> <trnsys-users at lists.onebuilding.org>:
>>
>>  RE: [TRNSYS-users] Calculating the PMV and PPD Index with TRNSYS
>>
>> Hi Alexander,
>>
>> Just open TRNBuild of a building, select Zone, and in the top right 
>> side of the window, there is a Green comfort symbol.
>>
>> In this Comfort manager, you can select new and define different 
>> factors accordingly.
>>
>> Also, for the outputs, just open output manager, select zone and in 
>> comfort outputs, you can define outputs for PMV and PPD.
>>
>> Best Regards
>>
>>
>> ____________________________
>>
>> *M.Sc. Bharat Chhugani*
>>
>> Institut für Solarenergieforschung GmbH
>>
>> Am Ohrberg 1
>>
>> D-31860 Emmerthal
>>
>>
>>
>>     -----Original message-----
>>     *From:* Alexander Schneider via
>>     TRNSYS-users <trnsys-users at lists.onebuilding.org>
>>     *Sent:* Friday 3rd April 2020 17:51
>>     *To:* trnsys-users at lists.onebuilding.org
>>     *Cc:* Alexander Schneider <alexander-pirmasens at web.de>
>>     *Subject:* [TRNSYS-users] Calculating the PMV and PPD Index with
>>     TRNSYS
>>
>>     Dear TRNSYS Community,
>>
>>     I try to calculate the PMV and PPD Index with TRNSYS using the Type 56. Can anyone explain me how I get and where I get the results of the PMV and PPD using Type 56? I have made a 3D Room Model with sketchup and defined all the layers for the building in TRNBuild. Now I want to put in some parameters and depending on them calculating the PMV and PPD. But I don’t know where I get the results vor the PMV and PPD.
>>
>>     I hope someone can help me.
>>     Thank you in advance for your help!
>>
>>
>>
>>     _______________________________________________
>>     TRNSYS-users mailing list
>>     TRNSYS-users at lists.onebuilding.org
>>     http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>>
>> ¥2019 ISFH [1546297200]_______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200403/1ab74ad6/attachment.htm>


More information about the TRNSYS-users mailing list