Erik,
Did you connect the input up to the equation? If so, I suspect it has to do with the AND. Simply multiply your two conditions together. X = GT() * LT(). But be aware that if the term you are watching is dynamic (depends on other things in the simulation) then your approach may lead to non-convergence problems. If this is the case, you may want to use a differential controller or two.
Jeff
> On Apr 29, 2020, at 9:51 AM, Erik Eriksson via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
> Hi!
>
> I want the AUX to be ON if the reference flow (ILS_out) is between 43-55°C. What am I doing wrong here?
>
>
> <E9D364CF91F24E7DB07B0F2A128B5959.png>
> Med vänliga hälsningar Erik
>