[TRNSYS-users] shading calculation
Marion Hiller
Hiller at Transsolar.com
Mon Sep 30 23:55:57 PDT 2019
Karol,
you don't need to turn on "detailed radiation mode" for a zone for generating and using a shading mask.
If "standard radiation mode" is selected for all zones and you generate shading/insolation mask, there will be a shading mask generated only.
If you run the simulation there is a notice in the *.log / *.lst file :
*** Notice at time : 0.000000
Generated by Unit : 56
Generated by Type : 56
Message : Shading mask file *.shm for external windows exists and will be used.
In addition, you can define a geometric shading output for checking.
In many cases, the geometric shading has a significant impact but not the geometric distribution of direct solar radiation.
Kind regards,
Marion
-----------------------------------------------------------------------------------------------------------------------------------------------------------
Dipl.-Ing. Marion Hiller
TRANSSOLAR Energietechnik GmbH
Stuttgart - Munich - New York - Paris
t: +49.711.67976.0<tel:%2B49.711.67976.27> f: +49.711.67976.11<tel:%2B49.711.67976.11>
www.transsolar.com/<http://www.transsolar.com/>
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347 / Steuernummer: 99073/00911 / USt-IdNr.: DE 152272639
Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag von David BRADLEY via TRNSYS-users
Gesendet: Montag, 30. September 2019 20:25
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: David BRADLEY <d.bradley at tess-inc.com>; Karol BANDURSKI <karol.bandurski at put.poznan.pl>
Betreff: Re: [TRNSYS-users] shading calculation
Karol,
Would it be possible to activate the detailed radiation model only for certain critical zones in the building? These might be zones that have a lot of windows for the given floor area.
kind regards,
David
On 09/24/2019 05:33, Karol BANDURSKI via TRNSYS-users wrote:
Dear Experts,
My goal is to get solar gain reaching each zone of my multiunit residential building. I need to take into account shading of surrounding buildings and self-shading.
I have prepared appropriate model in SketcUp (.idf enclosed).
It seems to me that .shm file is enough for my goal. But detailed beam radiation calculation need also .ism file for each considered zone.
My computer is not manage to create .ism files, I have only .shm file (enclosed).
Is there any way to get this solar gains, based only on .shm?
Simplification of building model are not solution for me... (I have simplified it as much as possible and each change of geometry could generate whole model error).
Kind regards,
Karol Bandurski
--------------------------------------------------------------------
Karol BANDURSKI M. Sc.
Faculty of Civil and Environemntal Engeneering
Division of Heating, Air Conditioning and Air Protection
Poznan University of Technology
www.put.poznan.pl/~karol. bandurski<http://www.put.poznan.pl/~karol.bandurski>
https://www.researchgate.net/profile/Karol_Bandurski
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191001/a6b0afe7/attachment.htm>
More information about the TRNSYS-users
mailing list