[TRNSYS-users] Temperature difference

David BRADLEY d.bradley at tess-inc.com
Wed Mar 20 11:34:17 PDT 2019


Michele,

   it is a bit hard to see the picture but it looks to me as though the 
TGROUND input is unconnected and set to an initial value of 0. That 
means that your building thinks that the ground temperature is 
constantly 0C.

kind regards,

  David


On 03/20/2019 03:52, Michele Vella wrote:
> Hi David
> I checked for links between the TGround and it is not linked with 
> anything. How this can be? I used the multizone template and entered 
> the weather from Meteonorm files.
> image.png
>
> On Mon, 18 Mar 2019 at 18:14, David BRADLEY <d.bradley at tess-inc.com 
> <mailto:d.bradley at tess-inc.com>> wrote:
>
>     Michele,
>
>     Check your assumptions about ground coupling. It sounds as though
>     perhaps the ground temperature beneath the church is set to
>     something unrealistically low.
>
>     kind regards,
>
>      David
>
>
>     On 03/17/2019 04:52, Michele Vella via TRNSYS-users wrote:
>>     Hi im modeling a church modeled as an atrium. But the lower part
>>     of the church is showing really low temperatures, in summer even
>>     difference of 10 degrees difference from the outside. What could
>>     be the reason? as the upper parts of the church shows more a
>>     realistic results
>>
>>     Regards
>>     Michele Vella.
>>
>>     _______________________________________________
>>     TRNSYS-users mailing list
>>     TRNSYS-users at lists.onebuilding.org  <mailto:TRNSYS-users at lists.onebuilding.org>
>>     http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>     -- 
>     ***************************
>     David BRADLEY
>     Principal
>     Thermal Energy Systems Specialists, LLC
>     3 North Pinckney Street - suite 202
>     Madison, WI  53703 USA
>
>     P:+1.608.274.2577
>     F:+1.608.278.1475
>     d.bradley at tess-inc.com  <mailto:d.bradley at tess-inc.com>
>
>     http://www.tess-inc.com
>     http://www.trnsys.com
>
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190320/c8c13153/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 75590 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190320/c8c13153/attachment-0002.png>


More information about the TRNSYS-users mailing list