[TRNSYS-users] (no subject)
David BRADLEY
d.bradley at tess-inc.com
Tue Mar 19 11:42:27 PDT 2019
Do I assume correctly that there is also a load flow on the DHW tank and
that the problem is you need a third set of inlet / outlet ports in the
tank?
If that is the case then you have two options. One is that if you have
access to the TESS Thermal Storage library then you can use Type534,
which allows you to define more than two pairs of inlet/outlet ports.
The other is that you will need to put a flow splitter (Type11) at the
load outlet of Type4 and a flow mixer (Type11 also) at the load side
inlet of the tank. The load flow through the tank will be the sum of the
hot water load and the energy dump flow. You will need to control the
flow splitter so that the correct amount of liquid goes to the DHW load
and the correct amount goes to the energy dump.
kind regards,
David
On 03/19/2019 12:14, berkane ahlem via TRNSYS-users wrote:
> Hello,
> I coupled the DHW tank outputs (temperarure + flow rate) to heat
> source with the solar collector , and (temperature + flow rate) to
> load for the distribution of DHW.when the average temperature of
> DHW exceeds the set point the circulation pump transfers the excess
> heat of DHW tank type (4b) to the borehole ,how can i linked
> circulation pump with storage tank for evacuate excess energy
> Best ragards
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190319/349e423b/attachment.htm>
More information about the TRNSYS-users
mailing list