[TRNSYS-users] Fwd: coupling air flow
David BRADLEY
d.bradley at tess-inc.com
Mon Mar 4 12:29:30 PST 2019
Michele,
There are two tools available for determining the quantity of
coupling airflow. One is Type97 (or Type98) (both of which are links
between TRNSYS and a freely available software tool called CONTAM). The
other is a commercially available TRNSYS add-on called TRNFlow. The idea
behind both is that the Trnsys building thermal model (Type56) provides
zone temperatures to the airflow model (CONTAM or TRNFlow). The airflow
model takes those temperatures (as well as ambient conditions and a
certain amount of building geometry with which the thermal model is not
usually concerned) and computes the corresponding interzonal air flows.
These are passed back to Type56, which recomputes zonal temperatures.
Iteration continues until both the thermal and airflow models agree.
kind regards,
David
On 03/04/2019 12:50, Michele Vella via TRNSYS-users wrote:
>
>
> Hi, I m designing a church with different thermal zones and the common
> surfaces are set to virtual surface. I activated the coupling . What
> would be the ideal coupling air flow?
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190304/3ba0d011/attachment.htm>
More information about the TRNSYS-users
mailing list