[TRNSYS-users] Weather data
David BRADLEY
d.bradley at tess-inc.com
Tue Jan 22 08:25:50 PST 2019
Siliang and Mohammad,
I may be misunderstanding what you are doing but if you are patching
measured temperature data into an existing "standard" weather data file
so that you can use the standard weather file's solar radiation then I
would urge being /very /cautious about this. You can easily end up with
very unrealistic data. In summer you could easily end up with the solar
saying that the day was very clear but a low temperature coming from a
period that was actually quite cloudy during that interval in your
actual data.
It sounds as though you are being careful about replacing both the dry
and wet bulb temperatures (as well as RH). If you only replace drybulb
temperatures without taking care of wet bulb, dew point, and RH then all
the humdity data in the file will be wrong.
kind regards,
David
On 01/22/2019 03:33, Siliang Yang wrote:
>
> Hi Mohammad,
>
> I’ve been using Type15-3 for my model though it is in TRNSYS17.
>
> Basically I used Elements (an open source) to modify the variables of
> the weather data (epw. format) such as WB/DB temperature and RH etc,
> of which you could easily edit any periods of the year. Then, I
> imported the modified epw. file into Type15-3 of my TRNSYS model, and
> it works properly and I’ve validated against the measured weather data
> as well. I’m not so sure if it is applicable for the case in TRNSYS15,
> but you might have a try.
>
> Hope it helps..
>
> Best regards,
>
> Siliang
>
> *Siliang Yang*
>
> /PhD Candidate and Casual Academic, UNSW Built Environment /
>
> Room 6007, Red Centre West Wing
>
> UNSW AUSTRALIA
>
> UNSW SYDNEY NSW 2052 AUSTRALIA
>
> T:+ 61 (2) 9385 6372 M: 0415 680 589
>
> www.be.unsw.edu.au <http://www.be.unsw.edu.au/>
>
> CRICOS Provider Code 00098G
>
> UNSW007F-Email-Signature-Image-2
> <https://www.be.unsw.edu.au/utzonlectures/emailsig>
>
> Follow us:
>
> facebookesig <http://www.facebook.com/UNSWBE>twitteresig
> <http://twitter.com/UNSWBuiltEnv>Instagramesig
> <http://instagram.com/unswbe>Web-Google-plus-Metro-icon-esog
> <http://plus.google.com/103377744913804443069>linkedinesig
> <http://www.linkedin.com/groups/UNSW-Built-Environment-6616950>flickresig
> <http://www.flickr.com/photos/unswbuiltenvironment/>youtubeesig
> <https://www.youtube.com/unswbuiltenvironment>
>
> This email and any attachment(s) transmitted with it are intended
> solely for the use of the addressee(s) and may contain information
> that is confidential or subject to legal privilege. If you receive
> this email in error, please disregard the contents of the email and
> attachment(s), delete them and notify the sender immediately. Please
> note that any copying, distribution or use of this email is
> prohibited. Any views expressed in this message are those of the
> individual sender, except where the sender expressly, and with
> authority, states them to be the view of The University of New South
> Wales. Before opening any attachments, please check for viruses. UNSW
> ABN 57 195 873 179..
>
> //
>
> /Think Green: Please consider the environment before printing this email./
>
> *From:*TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Mohammad Rezvanpour via TRNSYS-users
> *Sent:* Tuesday, 22 January 2019 6:43 PM
> *To:* TRNSYS users mailing list at OneBuilding.org
> <trnsys-users at lists.onebuilding.org>; David BRADLEY
> <d.bradley at tess-inc.com>
> *Cc:* Mohammad Rezvanpour <moh.rzv at gmail.com>
> *Subject:* [TRNSYS-users] Weather data
>
> Dear all,
>
> I want to simulate a photovoltaic panel, and I need weather data for
> Nov-Dec 2018. However, I could not find any TYPE to enter temperatures
> there or use updated data. It should be noted that my TRNSYS version
> is 15.
> How can I have updated temperature data or simply put the temperatures
> manually which I got from the Internet?
>
> Best,
> Mohammad
>
> --
>
> Regards.
>
> M.Sc. student of Energy and Environmental Engineering at University of
> Tehran
>
> Hand-Phone: +989303037373
> University Email account: m.rezvanpour at ut.ac.ir
> <mailto:m.rezvanpour at ut.ac.ir>
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3609 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 840 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0014.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 841 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 898 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 929 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0017.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 907 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0018.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 955 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0019.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 924 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190122/44eea642/attachment-0020.jpg>
More information about the TRNSYS-users
mailing list