You'll need to use a forcing function and set the non-summer months to a
value of 1 and the summer months to a value of 0. Then simply use an
equation and multiply the control signals together: 

On_Off_Pump = NotSummer * Type2ControlSignal 

where NotSummer is an equation connected to the Type 14 forcing function
and Type2ControlSignal is an equation connected to the output of the
Type 2 differential controller. Then simply connect the On_Off_Pump
equation to the input control signal for the pump. 

Jeff 

---
Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com

On 12/06/2019 1:41 pm, Emre Arpaci via TRNSYS-users wrote: 

> hi trnsys user 
> good weekend wishes 
> 
> I m controlling a pump with type 2b. I want to do that my pump would control with type 2b but in summer season (june ,july august) the pump would always off. 
> 
> Can I do this with trnsys and how ? 
> I shortly mean 
> 9 months contro with differential element type 2 
> summer season is off. 
> 
> regards 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
 

Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191206/03fab628/attachment.htm>


More information about the TRNSYS-users mailing list