[TRNSYS-users] Creating the data file for the Air Source Heat Pump (Type 119)

Audun Bull Kristiansen audun.bull at hotmail.com
Sun Dec 15 23:55:21 PST 2019


I use the Air Source Heat Pump (ASHP) unit Type 119c in a simulation of a container building in TRNSYS 18, since this seems to be the only ASHP type available. I need to add the two external .dat- files that contains the heating and cooling performance data, respectively. I read in “09-Tutorials” page 163-164 that:

“The ASHP component model requires a data file that includes the performance map for the piece of equipment. This performance map is unique to the exact piece of equipment that is being modeled and you will need to produce this file from the manufacturer’s performance data for the specific equipment being modeled.”

The component does not extrapolate beyond the data range provided, so we need to include data for outdoor temperatures between -5 °C and 40 °C (Shanghai climate). The indoor temperature is expected to be between -5 °C and 50 °C (due to that the heat pump is turned off when no one is at home).

I read “10.2.3.4 Resizing the PTHP Units” that says that the recommended method is to find a manufacturer of PTHP units online and to search through the available product literature to find a PTHP that has a capacity as close as possible without being less than the peak total cooling or heating load required by the zone that will be conditioned by the PTHP. Do someone know any such online source that contain adequate information where I can search for a similar product?

Or do you recommend me to go for the second approach, to renormalize the example files ASHP_Cooling.dat and ASHP_Heating.dat that comes with TRNSYS to a different rated capacity? But my highest “return air dry bulb temperature” and “Outdoor dry bulb temperature” are far higher than in these example files, so then I need to extrapolate the data. And how do I locate the performance point in ASHP_Cooling.dat that corresponds to the rated point, as described in 10.2.3.4?

I have also tried to model with ideal heater and cooler and divide the electric energy use for heating and cooling by their respective seasonal COP, but that is not accurate enough since I need to take into account the variation in COP over the year.

The heat pump that we have installed and want to model is GREE KFR-35W/FNhD02-A1 outdoor unit (corresponding to indoor unit model KFR-35GW/(35592)FNhAa-A1) which has the following performance data:

  *   Cooling power (rated/min./max.): 3500/200/4200 W
  *   Heating power (rated/min./max.): 4900/500/5600 W +1000 W (Additional electrical heating)
  *   Cooling input power (rated/min./max.): 840/90/1300 W
  *   Heating input power (rated/min./max.): 1450/120/1700 W
  *   Additional electrical heating input power: 1000 W
  *   Cooling seasonal COP: 5.33
  *   Heating seasonal COP: 3.53
  *   Yearly COP: 4.53

I tried to contact the manufacturer to get input data for the files and sent them the instructions from “4 Mathematical Reference” page 174-175 “Data Files” and the two  example files ASHP_Cooling.dat and ASHP_Heating.dat that comes with TRNSYS 18. The data they sent me, however, was not for constant air flow rates. For instance, for heating mode they sent me similar information as in the table below for various temperatures. The problem is that these data does not keep a set of fixed temperatures and air flow rates, like in the example files.

indoor air temperature  outdoor air temperature Total capacity (kJ/h)    Power consumption(kJ/h)        Air Flow Rate(l/s)      Return air dry bulb(℃)
30℃     28℃/RH50%       762     127     163     44.5
24℃/RH55%       706     128     163     43.3
20℃/RH59%       785     169     163     44.9
15℃/RH65%       992     284     161     49.2
11℃/RH75%       1078    362     160     51.2
7℃/RH85%        1085    418     160     51.3
2℃/RH85%        1063    485     159     51


Audun