Dear Van Long LE,
All airnodes of a Trnflow network have to be connected by links.
There is missing a link between Zone_E5 and zone_F5.
In addition, for TRNFlow you need to define the "air inlet" AND "air outlet". The outlets is missing.
Kind regards,
Christoph
__________________________________________________________________________________________________
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
http://www.transsolar.com<http://www.transsolar.com/>
Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Stuttgart - München - New York - Paris
Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle
Eingetragen beim Amtsgericht Stuttgart HRB 23347,
Steuernummer: 99073/00911,USt-IdNr.: DE 152272639
The simulation project you have sent will be stored on the local servers of Transsolar Energietechnik GmbH for the duration of the project support. Our employees are obliged by us to confidentiality. After this period, all project-related data is deleted.
The storage of your personal e-mail and other contact information is based on the mutual interest in the execution of this traffic and on a mutual business contact. If you have any questions, please contact our data protection officer at privacy at transsolar.com<mailto:privacy at transsolar.com>. Our privacy policy can be found here<http://www.trnsys.de/docs/userservice/userservice_dataprivacy_en.htm>.
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag von Long Le-Van via TRNSYS-users
Gesendet: Freitag, 28. September 2018 08:32
An: trnsys-users at lists.onebuilding.org; trnsys-users-request at lists.onebuilding.org
Cc: Long Le-Van <long.le-van at outlook.com>
Betreff: [TRNSYS-users] need help for trnflow error
Dears,
Could you please tell me why I cannot create the airflow network like below for my two-zones building
[cid:image001.png at 01D45A3E.DA9FB980]
Indeed, I received the following error
[cid:image002.png at 01D45A3E.DA9FB980]
Thank you very much for your help!
-----------
Van Long LE
Research Engineer
Energy & Building
Cenaero ASBL
Your trustworthy R&T partner
in modeling and numerical simulation
Tel.: +32 71 910 993
Fax: +32 71 910 931
Cenaero Headquarters
Rue des Frères Wright, 29
6041 Gosselies
Belgium
Visit our web site: www.cenaero.be<http://www.cenaero.be>
+-+-+- www.cenaero.be/disclaimer<http://www.cenaero.be/disclaimer> +-+-+-
Please consider the environment before printing this e-mail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181002/bc9342dd/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 22356 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181002/bc9342dd/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7474 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181002/bc9342dd/attachment-0003.png>
More information about the TRNSYS-users
mailing list