[TRNSYS-users] TRNSYS-users Digest, Vol 167, Issue 22

hotline hotline at Transsolar.com
Wed Nov 28 02:37:59 PST 2018


Dear Wang Yang,

the difference is that in “2D-model” you used the external calculation of radiation data and in “3D-model” you used the internal calculation.
The option “Internal calculation of radiation data” reduces the required input data from the weather data component significantly. To use this feature only the solar zenith (Input 5) has to be connected to the weather data component Type 15, Type16, Type99.
If the option “external calculation of radiation data” is selected, three inputs of incident radiation to the Type 56 Trnsys component will be required. This is generally provided by the weather component.
The internal as well as the external calculation of radiation data are using the same radiation calculation routine from kernel.
The orientation named H_0_0 is automatically recognized as the horizontal radiation. If this orientation doesn’t exist, no diffuse geometric shading and daylight calculation is performed.

For more Information, please have a look into the … \Documentation\05-MultizoneBuilding.pdf  -> The Project Dialog Box

Best,
Christoph

Von: WANG Yang <wanghongyang1767 at gmail.com>
Gesendet: Dienstag, 27. November 2018 08:53
An: trnsys-users at lists.onebuilding.org; hotline <hotline at Transsolar.com>
Betreff: Re: TRNSYS-users Digest, Vol 167, Issue 22

Dear Madam or Sir,

I hope all is well.

I have the new questions between old 2D simulation and current 3D simulation (TRNSYS3D):

1) after I imported *idf file to simulation studio, the link between Radiation Equation and Type56 is lack of many inputs and outputs, see below pictures. Furthermore, I cannot also Define new inputs from TRNBuild e.g. IT N 180 90, IT S 0 90 etc. Thus, I cannot use TRNSYS 3D model to repeat/simulate my previous project.
How to deal with this problem? Super thanks

Br.

Yang

[image.png] 2D model
[image.png]3D model
[image.png]TRNBuild Settings for Inputs

<trnsys-users-request at lists.onebuilding.org<mailto:trnsys-users-request at lists.onebuilding.org>> 于2018年11月24日周六 上午5:22写道:
Send TRNSYS-users mailing list submissions to
        trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>

To subscribe or unsubscribe via the World Wide Web, visit
        http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

or, via email, send a message with subject or body 'help' to
        trnsys-users-request at lists.onebuilding.org<mailto:trnsys-users-request at lists.onebuilding.org>

You can reach the person managing the list at
        trnsys-users-owner at lists.onebuilding.org<mailto:trnsys-users-owner at lists.onebuilding.org>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:

   1. Re: QTSABS vs QSOLTR (Karol Bandurski)



---------- Forwarded message ----------
From: Karol Bandurski <karol.bandurski at put.poznan.pl<mailto:karol.bandurski at put.poznan.pl>>
To: "'hotline'" <hotline at transsolar.com<mailto:hotline at transsolar.com>>, "'TRNSYS users mailing list at OneBuilding.org'" <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>>
Cc:
Bcc:
Date: Fri, 23 Nov 2018 09:39:10 +0100
Subject: Re: [TRNSYS-users] QTSABS vs QSOLTR
Dear Christoph,

Thank you for your response!

The problem is that, it seems to me, that I don’t have internal shading, so QSOLTR should equal QTSABS. Am I right?

How should I set window type and external devices to get QSOLTR=QTSABS?

Kind regards,
Karol

From: hotline [mailto:hotline at Transsolar.com<mailto:hotline at Transsolar.com>]
Sent: Thursday, November 22, 2018 4:57 PM
To: TRNSYS users mailing list at OneBuilding.org
Subject: Re: [TRNSYS-users] QTSABS vs QSOLTR

Dear Karol,

QSOLTR is the total shortwave solar radiation transmitted through external windows and internal shading.
QTSABS also includes the secondary heat flux which includes the convection of internal shader.

Hope that clarifies your energy balance a bit.

Best,
Christoph

Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org<mailto:trnsys-users-bounces at lists.onebuilding.org>> Im Auftrag von Karol Bandurski via TRNSYS-users
Gesendet: Mittwoch, 21. November 2018 16:42
An: trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>
Cc: Karol Bandurski <karol.bandurski at put.poznan.pl<mailto:karol.bandurski at put.poznan.pl>>
Betreff: [TRNSYS-users] QTSABS vs QSOLTR

Dear All,

I am going to find whole solar gain which come to zone throug windows.
There are two outputs that I consider: QTSABS and QSOLTR.

It seems to me that bigger should be QSOLTR, because it is shortwave radiation transmitted through window (but not kept 100% in air node).
The QTSABS is what exactly has been kept - has been absorbed by inside surfaces.
But it is appear that QTSABS > QSOLTR…

Could you write me what is right interpretation of those outputs?

Kind regards,
Karol

--------------------------------------------------------------------
Karol BANDURSKI M. Sc.
Faculty of Civil and Environemntal Engeneering
Division of Heating, Air Conditioning and Air Protection
Poznan University of Technology
https://www.researchgate.net/profile/Karol_Bandurski
www.put.poznan.pl/~karol.bandurski<http://www.put.poznan.pl/~karol.bandurski>

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181128/3c7e575e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 21824 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181128/3c7e575e/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 98679 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181128/3c7e575e/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 54737 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181128/3c7e575e/attachment-0008.png>


More information about the TRNSYS-users mailing list