[TRNSYS-users] QTSABS vs QSOLTR
hotline
hotline at Transsolar.com
Thu Nov 29 05:29:34 PST 2018
Dear Karol,
I have to confess that this is a little confusing.
For better understanding of the differences of QSOLTR and QTSABS it is important to understand the considered "parts".
QSOLTR is the total shortwave solar radiation transmitted through all external windows including shading device into the airnode.
Then in the airnode this radiation is distributed to surfaces (taking into reflection). (For simplicity reasons we assume that there are no adjacent windows).
As a results QSOLTR is either
a) immediately transferred as convective heat gain to the internal air (= Qsolair, doesn't exist in Trnsys 17) or is
b) absorbed by walls or
b) is absorbed by windows (panes, frame and internal shading devices) as radiation leaves (!) the airnode to the outside or
c) is transmitted to the outside (= QTSOUT, NType 73)
QTSABS (NType 75) consists of
1. solar radiation is absorbed by walls and
2. the secondary heat flux of windows (panes, frame and internal shading devices) ( = QSEC, NType 56).
In this case the secondary heat flux is the part of solar radiation that is absorbed by windows when solar radiation is entering and leaving the airnode
and going inside to the airnode.
Thus, QSOLTR and QTSABS consider different parts of the solar radiation.
I assume you are looking something like QSOLTR - QTSOUT.
I hope this explanation helps.
Kind regards,
Marion
Von: Karol Bandurski <karol.bandurski at put.poznan.pl>
Gesendet: Freitag, 23. November 2018 09:39
An: hotline <hotline at Transsolar.com>; 'TRNSYS users mailing list at OneBuilding.org' <trnsys-users at lists.onebuilding.org>
Betreff: RE: [TRNSYS-users] QTSABS vs QSOLTR
Dear Christoph,
Thank you for your response!
The problem is that, it seems to me, that I don't have internal shading, so QSOLTR should equal QTSABS. Am I right?
How should I set window type and external devices to get QSOLTR=QTSABS?
Kind regards,
Karol
From: hotline [mailto:hotline at Transsolar.com]
Sent: Thursday, November 22, 2018 4:57 PM
To: TRNSYS users mailing list at OneBuilding.org
Subject: Re: [TRNSYS-users] QTSABS vs QSOLTR
Dear Karol,
QSOLTR is the total shortwave solar radiation transmitted through external windows and internal shading.
QTSABS also includes the secondary heat flux which includes the convection of internal shader.
Hope that clarifies your energy balance a bit.
Best,
Christoph
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org<mailto:trnsys-users-bounces at lists.onebuilding.org>> Im Auftrag von Karol Bandurski via TRNSYS-users
Gesendet: Mittwoch, 21. November 2018 16:42
An: trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>
Cc: Karol Bandurski <karol.bandurski at put.poznan.pl<mailto:karol.bandurski at put.poznan.pl>>
Betreff: [TRNSYS-users] QTSABS vs QSOLTR
Dear All,
I am going to find whole solar gain which come to zone throug windows.
There are two outputs that I consider: QTSABS and QSOLTR.
It seems to me that bigger should be QSOLTR, because it is shortwave radiation transmitted through window (but not kept 100% in air node).
The QTSABS is what exactly has been kept - has been absorbed by inside surfaces.
But it is appear that QTSABS > QSOLTR...
Could you write me what is right interpretation of those outputs?
Kind regards,
Karol
--------------------------------------------------------------------
Karol BANDURSKI M. Sc.
Faculty of Civil and Environemntal Engeneering
Division of Heating, Air Conditioning and Air Protection
Poznan University of Technology
https://www.researchgate.net/profile/Karol_Bandurski
www.put.poznan.pl/~karol.bandurski<http://www.put.poznan.pl/~karol.bandurski>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181129/98ce1ec5/attachment-0001.html>
More information about the TRNSYS-users
mailing list