[TRNSYS-users] QTSABS vs QSOLTR
    Karol Bandurski 
    karol.bandurski at put.poznan.pl
       
    Tue Nov 27 02:35:02 PST 2018
    
    
  
Dear Christoph,
 
Thank you for your response!
 
The problem is that, it seems to me, that I don't have internal shading, so
QSOLTR should equal QTSABS. Am I right?
 
How should I set window type and external devices to get QSOLTR=QTSABS?
 
Kind regards,
Karol
 
From: hotline [mailto:hotline at Transsolar.com] 
Sent: Thursday, November 22, 2018 4:57 PM
To: TRNSYS users mailing list at OneBuilding.org
Subject: Re: [TRNSYS-users] QTSABS vs QSOLTR
 
Dear Karol,
 
QSOLTR is the total shortwave solar radiation transmitted through external
windows and internal shading.
QTSABS also includes the secondary heat flux which includes the convection
of internal shader.
 
Hope that clarifies your energy balance a bit.
 
Best,
Christoph
 
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> Im Auftrag
von Karol Bandurski via TRNSYS-users
Gesendet: Mittwoch, 21. November 2018 16:42
An: trnsys-users at lists.onebuilding.org
Cc: Karol Bandurski <karol.bandurski at put.poznan.pl>
Betreff: [TRNSYS-users] QTSABS vs QSOLTR
 
Dear All,
 
I am going to find whole solar gain which come to zone throug windows.
There are two outputs that I consider: QTSABS and QSOLTR.
 
It seems to me that bigger should be QSOLTR, because it is shortwave
radiation transmitted through window (but not kept 100% in air node).
The QTSABS is what exactly has been kept - has been absorbed by inside
surfaces.
But it is appear that QTSABS > QSOLTR.
 
Could you write me what is right interpretation of those outputs?
 
Kind regards,
Karol
 
--------------------------------------------------------------------
Karol BANDURSKI M. Sc.
Faculty of Civil and Environemntal Engeneering
Division of Heating, Air Conditioning and Air Protection
Poznan University of Technology
https://www.researchgate.net/profile/Karol_Bandurski
 <http://www.put.poznan.pl/~karol.bandurski>
www.put.poznan.pl/~karol.bandurski
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181127/504bf7a6/attachment.html>
    
    
More information about the TRNSYS-users
mailing list