[TRNSYS-users] I: strange output for type 927
Jeff Thornton
thornton at tess-inc.com
Tue May 15 17:59:02 PDT 2018
Chiara,
If you have no heat transfer from the heat pump that means the device is off. And if the device is off then the outlet temperature is set to the inlet temperature. So if you’re seeing a large outlet temperature it means that you are giving the model a large inlet temperature. I suggest you review the TRACE command in TRNSYS and use it to figure out what may be going wrong with your simulation.
Jeff - TESS
Sent from my iPhone
> On May 15, 2018, at 1:40 PM, chiara pinto via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
>
> Inviato da Posta per Windows 10
>
> Da: chiara pinto via TRNSYS-users
> Inviato: lunedì 14 maggio 2018 20:17
> A: trnsys-users at lists.onebuilding.org
> Cc: chiara pinto
> Oggetto: [TRNSYS-users] strange output for type 927
>
> Hi everyone,
> i’m using type 927 to simulate a water to water heatpump. I have write the input file and i have modify the input schedule in trnsys, but ,when i run the simulation , i have strange value: for example my oulet load temperature= 1.6*10^8 and this is not normal. I have the same problem if i use the input file that trnsys give me as example with its default values.
> One other problem is that the heat pump seems to be off because heat transfer to load end heat transfer from source are zero. There is a type to impose that heat pump had to be on from 8.00 am to 17.00 pm?
>
> I really don’t understand where the problem is.
> Has anyone a solution for this problem?
>
> Thanks for your help,
> Best regards,
> Chiara
>
>
> Inviato da Posta per Windows 10
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180515/fff4b930/attachment.htm>
More information about the TRNSYS-users
mailing list