[TRNSYS-users] message 126

David BRADLEY d.bradley at tess-inc.com
Tue May 8 12:11:11 PDT 2018


Chiara,

  That is a bad default value. The scale factor should be set to 1.

kind regards,

  David



On 05/08/2018 13:43, chiara pinto via TRNSYS-users wrote:
>
> Hi everyone,
>
> i’m using type 927 to simulate a water to water heat pump but when i 
> start the simulation an error like this occurs:
>
> TRNSYS Message  126 : The referenced Unit has a bad imput value
> Reported information : Input # 7, Reported Problem. The scale factor 
> must be above 0.
>
> The problem is that i have not changed this parameter and it is equal 
> to 0.
>
> Has anyone experienced this problem and knows how to fix it?
>
> Best regards,
>
> Chiara
>
> Inviato da Posta <https://go.microsoft.com/fwlink/?LinkId=550986> per 
> Windows 10
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180508/c9d72b7d/attachment-0001.html>


More information about the TRNSYS-users mailing list