<How can i to specify (N_Sources * n_loads) data points>
The data file takes a row of source temperatures and a row of load
temperatures. If there are 7 source and 6 load temperatures then you
will need to specify 42 lines of data. Please refer to the example data
files for the Type 668 model and the description of Type 42 - a
component that uses a similar data file structure and explains in great
detail how to set up the files.
Jeff
---