[TRNSYS-users] small mass flow in TABS
David BRADLEY
d.bradley at tess-inc.com
Mon Jun 4 10:06:08 PDT 2018
Karol,
I do not think that the problem with the matrix inversion and the low
flow rate in the active layer are necessarily related. I'm not sure what
to suggest about the matrix inversion. The active layer model has a
minimum allowable flow rate that is based on pipe spacing, the thickness
of the layer(s) in which the pipes are embedded and the area of the
floor. If you want to give a lower flow rate then you need to segment
the floor, which means treating the floor like it was a few floors in
series. Enter the desired minimum mass flow rate in the active layer
definition screen. If it is below the minimum "allowed" mass flow rate
then you'll have the option to segment the floor.
kind regards,
David
On 06/04/2018 01:58, Karol Bandurski via TRNSYS-users wrote:
>
> Dear Experts
>
> I have problem with simulation TABS with specific mass flow rate about
> 5.4 kg/hm2.
>
> There are two errors:
>
> 1)Specific fluid mass flow of active layer in surface 894 below
> minimum value of 8.90 kg/m2h Please, increase the minimum mass flow
> rate or use the autosegmentation feature of TRNBuild for subdividing
> the surface.
>
> 2)Subroutine INVERT was called from subroutine INVPAR with a singular
> matrix!
>
> I have increase number of loops 10 times but nothing change…
>
> It is possible to do simulation with so low mass flow rate?
>
> Kind regards,
> Karol
>
> --------------------------------------------------------------------
>
> Karol BANDURSKI M. Sc.
>
> Faculty of Civil and Environemntal Engeneering
>
> Division of Heating, Air Conditioning and Air Protection
>
> Poznan University of Technology
>
> https://www.researchgate.net/profile/Karol_Bandurski
>
> www.put.poznan.pl/~karol.bandurski
> <http://www.put.poznan.pl/%7Ekarol.bandurski>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180604/202afc5d/attachment.html>
More information about the TRNSYS-users
mailing list