When you define an ADJACENT wall (or floor/ceiling) between two zones
you have the ability to define a coupling air flow rate from each to the
other. You can set the flow rate as a constant, as a scheduled value, or
as an input. Type56 leaves it to you to determine how much air flows
back and forth between the zones.
The most correct way of determining the quantity of airflow is to use
an airflow modeling tool such as TRNFlow or Type97/CONTAM.
It is hard to answer your second question. The answer depends on what
metrics you are looking at. For instance, I would be surprised to see
the loads of the building change by 10% based on 1 zone or 2. However,
if you are looking at consumption of energy by an HVAC system then it is
possible, especially if you are using a single thermostat to control the
system.
kind regards,
David
On 01/24/2018 08:22, Alex moreno via TRNSYS-users wrote:
> Hi
>
> I have a doubt when i modeling a single family building with two floors,
> how i can connect the airchange between of two zones (first floor and
> second floor)
>
> another doubt is:
>
> Firstly i simulated the two floors us one zones, but now i simulate the
> buildign us two zones, the results of heating differ 2% respec of one
> zone building and differ cooling 10%, it is normally?
>
> regards
>
>
> Alex
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
More information about the TRNSYS-users
mailing list