Dear Massimiliano,

Personally, I don’t like editing weather data files. It is always confusing sooner or later.
Another option is the following:

  *   set in TRNbuild for the orientation the “calculation of radiation data” from “internal”  to “external by another component”
-> For the orientation 3 Inputs are required now: total radiation, beam radiation and incident angle
  *   define the orientation in Type 15 and link the outputs to an equation card
  *   In the equation card you can modified the radiation and link the output to Type 56

Kind regards,

Marion



Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von hotline via TRNSYS-users
Gesendet: Dienstag, 27. Februar 2018 09:54
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: hotline <hotline at Transsolar.com>
Betreff: Re: [TRNSYS-users] Solar Radiation with Type 56

Dear Massimiliano,

you can simply replace the solar radiation in the .ewp file by using a text editor or MS EXCEL. For more information about Type15 please read “03-ComponentLibraryOverview Manual, 3.4.14. Weather Data Reading and Processing” or “08-WeatherData Manual”.

Regards,
Christoph


Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von Tapp_fi Tappatrice Sigillatrice via TRNSYS-users
Gesendet: Samstag, 24. Februar 2018 12:30
An: trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>
Cc: Tapp_fi Tappatrice Sigillatrice <max.fi.screwcaps at gmail.com<mailto:max.fi.screwcaps at gmail.com>>
Betreff: [TRNSYS-users] Solar Radiation with Type 56

Dear Users,

I have a problem concerning type56. I created the model of the building I'm studying, with Google Sketchup, and through 3D Building Project
I put it on TRNSYS.





The TRNSYS program asks me to insert the TM2 file but without having it, I inserted the type15 file with the Florence EPW file in my possession.




Unfortunately I realized that in the EPW file the solar radiation is greater than the solar radiation recorded in 2016 by the Florence station.
So I ask you if there is a way to correct this radiation or if you can explain to me how type15 is connected to type56.

Kind regards

Massimiliano