[TRNSYS-users] Type 71 Evacuated tube collector - Control vs. overheating
maverickxxx1991
maverickxxx1991 at googlemail.com
Wed Feb 28 13:54:14 PST 2018
An embedded and charset-unspecified text was scrubbed...
Name: List File.txt
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180228/96c03428/attachment-0001.txt>
-------------- next part --------------
> Am 28.02.2018 um 20:35 schrieb Jeff Thornton via TRNSYS-users <trnsys-users at lists.onebuilding.org>:
>
> Maverick,
>
> Your 3rd control shuts off the pump when the collector temperature exceeds 110 C. But once the pump shuts off, the collector will stagnate and reach very high temperatures with no flow through the collectors. In this case, the 3rd control should probably sense the outlet temperature of the pipe leaving the collector and not the collector itself. This way you're getting the overheat protection when there is flow.
>
> As for the quick temperature rise in winter, I'll point out that Type 71 does not include the impact of mass. So temperatures will rise and fall very quickly. The TESS version of the evacuated tube model accounts for the mass and should behave much as you expect it to.
>
> Jeff
>
> ---
> Jeff Thornton
> President - TESS LLC
> 22 N. Carroll Street, Madison WI USA 53703
> Office: (608) 274-2577 Fax: (608) 278-1475
> www.tess-inc.com
> E-Mail: thornton at tess-inc.com
>
>
> On 02/26/2018 4:49 am, maverickxxx1991 via TRNSYS-users wrote:
>> Hi,
>> I?m using 2 type 71 and I get temperature up to 400?C if I use a
>> control. I have 3 Controllers of type 2b:
>> 1st looks if temperature of collector is higher than secondary inlet
>> of heat exchanger with hysteresis (7K and 4K)
>> 2nd looks for storage temperature (<95?C with hysteresis again ?On? at 90?C)
>> 3rd is for collector protection (collector temperature <110?C with
>> hysteresis again ?On? at 95?C)
>> The collector values are (0.688, 0.583, 0.003) (last in W/(m^2*K) and
>> W/(m^2*K^2)).
>> Test condition flow rate 0.02 kg/(s*m^2).
>> 2x86 m^2 area, no. in series 1, flow rate 2600 kg/hr.
>> So if the controls says out the temperature in the collectors rise up
>> to 400?C. Is it normal? How can I fix it? I even wondering about the
>> temperatures rising so fast also in winter from 15 to 80?C.
>> Thanks for help!
>> maverickxxx
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
More information about the TRNSYS-users
mailing list