[TRNSYS-users] REGARDING REFRIGERANT INFORMATION

David BRADLEY d.bradley at tess-inc.com
Mon Feb 5 07:58:49 PST 2018


Prof  Sodha,

   The absorption chiller models in TRNSYS are performance map models. 
They read capacity and COP as a function of the inlet and ambient 
conditions to which the chiller is subject at any given time. As such 
the type of refrigerant is built into the performance map. If there were 
a way that you could experimentally measure data and generate a 
performance map for the same chiller using two different refrigerants 
then you could use those two different performance maps in simulation to 
see the impact of changing the refrigerant.

kind regards,

  David



On 01/31/2018 04:11, DHAVALSINH SODHA via TRNSYS-users wrote:
> DEAR SIR/MA'AM,
>                HOW TO GET INFORMATION ABOUT REFRIGERANT USED IN 
> ABSORPTION CHILLER FOR EACH ? LIKE WHICH REFRIGERANT AND RELATED 
> PARAMETER ?
> MOST IMPORTANT HOW TO CHANGE THE REFRIGERANT IN CHILLERS...? IS IT 
> POSSIBLE ?
>
>
>
> -- 
> *Thanks & Regards*
> *Dhavalsinh R. Sodha **/(M.E. Thermal Engineering)/*
> *Assistant Professor , **Mechanical Department*
> *Faculty of Engineering & Technology ( PIT )*
> *(9898917008)*
> *_PARUL UNIVERSITY_*
> *P.O. Limda, Tal. Waghodia-391760, Vadodara, Gujarat , India
> Ph.: 02668-260430/260300
> Telefax: 02668-260201 , Website: www.parul.ac.in 
> <http://www.parul.ac.in/>*
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180205/b91c0a00/attachment.html>


More information about the TRNSYS-users mailing list