[TRNSYS-users] question

David BRADLEY d.bradley at tess-inc.com
Thu Aug 9 11:30:07 PDT 2018


Henri,

   I usually make a split of about 50% convective and 50% radiative for 
generic plug loads. I do not know specifically how a television breaks 
down. I'd guess it were somewhat more radiative than most appliances 
when it is on. You can always set the gain to be 100% radiative then do 
another run with it set to 100% convective and see if there are any 
noticeable differences in your annual results. If there aren't then the 
simulation is not sensitive to that particular assumption and you can 
not worry about spending time researching a really accurate value.

kind regards,

  David



On 08/06/2018 06:59, Henri Hounkpatin via TRNSYS-users wrote:
> Good evening everyone, I would like to ask, how we use "gain Type 
> Manager"
> for a 65W TV, what is its convective power and radiative power ?
> Regards,
>
> 2018-07-28 17:47 GMT+01:00 Henri Hounkpatin <orestahenrius at gmail.com 
> <mailto:orestahenrius at gmail.com>>:
>
>     Good evening everyone, I would like to ask, how we use the
>     histogram plotter on TRNSYS,
>     By the way, I want to have histogram output on TRNSYS, for example
>     the cooling energy demand.
>     Regards,
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180809/cb1c3e36/attachment.htm>


More information about the TRNSYS-users mailing list