We don't officially support TRNSYS 16 as it's two versions out of date.
But I took a quick look at your project and several things stood out
immediately. The first is that you are using a 1-hour time step. That
means your control decisions are made once an hour - likely the biggest
cause of your issues. Typically a sysytem like this should run at
around a 1-minute time step. The other thing I caught was that your
pump flow rates are only about a third of the minimum flow rate that the
heap pump expects. This will create a very large temperature difference
across both sides of the heat pump.
Jeff
---