These are the specifications of the heat pump on different temperature levels at the load side and the source side, typically you get them from manufacturer data. It makes no sense trying to calculate them on your own. The values in your example means that the heat pump has a cooling power of 49.94 kW and needs 9.1 kW of electric power when the temperature at the load side is -3.89 °C and the temperature at the source side is 7.22 °C.
Regards,
Matthias
From: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] On Behalf Of berkane ahlem via TRNSYS-users
Sent: Freitag, 27. April 2018 15:07
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: berkane ahlem <jinan.berkane at gmail.com>
Subject: [TRNSYS-users] (no subject)
Hello,sirs
I am using type 668 (water to water heat pump) for my TRNSYS
I was reading the external files but I don´t understand the meaing of this files
For example (total cooling(kw),and power(kw) at -3.89/7.22) it 49,94kw and 9.10 kw
How can i calulate them ,and how can i change this values
Thank you in advance