[TRNSYS-users] the simulation of a room
adnan rasheed via TRNSYS-users
trnsys-users at lists.onebuilding.org
Sun Sep 3 20:04:04 PDT 2017
HI jennefer,
1- i think check thickness of the wall you selected i mean if you made wall
with different materials while selecting thickness may be some problem.
2- The simulation START time must be an integer multiple of the >wall
TIMEBASE in BID or the program WILL NOT run correctly. For example, if the
wall timebase is 0.5 hours, the simulation >start time must be 0.0, 0.5,
1.0, 1.5 etc.
you can check time base from in (TRNSBuild- project window-- output)
check calculation heat transfer function's time base and in Simulation
studio control card check simulation time step
3- Type 56 can simulate a room no worries.
hope it will help this is what i know little about TRNSYS.
Regards
Adnan Rasheed
PhD student
On Mon, Sep 4, 2017 at 11:48 AM, WU Jennifer via TRNSYS-users <
trnsys-users at lists.onebuilding.org> wrote:
> Dear Trnsys users,
>
>
>
> I am a freshman, I use type 56 to iuput the parameters of a room,not two or more.then something is wrong, I have this message:
>
> "Error creating wall transfer function coefficients: unable to find a root after indication that a root exists. Maybe timebase is too small. Please,check the INF-file for futher instructions.
>
> I follow the instructions to re-get it and found no solution to any
> problems, my current distress is :
>
> 1: can type56 simulate a room? 2, if not, which type can simulate a room?
>
> Thanks in advance
>
> jennifer
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170904/1314ac21/attachment.htm>
More information about the TRNSYS-users
mailing list