I use Type36 in Mode 2 (air flowrate computed internally, glazing
transmittance as an input) to model a naturally vented Trombe wall.
I use the multi-layer detailed window model from Type56 to compute the solar
transmittance B3_QSTRNS/B3_QSEXT and U-value UWIN of the window (at each
time step).
Looking at the source code of Type36 I cannot figure out how the model
accounts for the inward-flowing portion of the solar radiation absorbed by
the window. Therefore I would rather provide SHGC
(B3_QSTRNS+B3_QSHFPR)/B3_QSEXT instead of solar transmittance as an input to
Type36.
The drawback being all this inward-flowing portion considered as radiation
absorbed by the massive wall. However the uncertainty (assuming all
inward-flowing portion is radiative) seems lower than totally neglecting the
inward-flowing portion.
Would somebody have a recommendation to share?