[TRNSYS-users] Output of the building

David BRADLEY via TRNSYS-users trnsys-users at lists.onebuilding.org
Sun May 14 20:18:17 PDT 2017


The outlet air temperature of the building is the air node temperature. 
Type56 does not have outputs for the mass flow rate of air out of a 
space because it assumes that all of the air that goes into a zone 
through one of the VENTILATION types also leaves that zone by the same 
mechanism. Thus you can take the Type697 output flow rate as the input 
flow rate to the fan that is moving air between the cooling coil and the 
zone.

Please note that if you are using CONTAM (Type97/Type98) or TRNFlow the 
assumption that VENTILATION air supply and return is balanced no longer 
necessarily true.

kind regards,

  David



On 05/12/2017 23:51, Raouf Bilal via TRNSYS-users wrote:
> Dear colleagues,
>
>
> I heve a difficul to link the building (TYpe 56) and the type 697a 
> (Performance Map Cooling Coil)
> Ican't find a Tair  and flow rate output of the building
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170514/3aec8aff/attachment-0003.htm>


More information about the TRNSYS-users mailing list