[TRNSYS-users] (no subject)

Jeff Thornton via TRNSYS-users trnsys-users at lists.onebuilding.org
Mon May 8 08:09:31 PDT 2017


Javier,

Please post a screen capture of your system so we can see the flow connections.  I have an idea as to what may be wrong.

Jeff 

Sent from my iPhone

> On May 6, 2017, at 5:37 PM, Javier Vega via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
> 
> Hi TRNSYS users,
> 
> I'm experiencing a weird issue. I'm testing a simple system where I have a heat pump (Type 941) and solar collectors (Type 538) coupled  to a Vertical Storage Tank via heat exchangers, modelled with Type 534. The tank is connected to a closed loop to a radiant floor.
> 
> I have the control system setted this way:
> 
> -The collector's circuit works if they can gain energy. ON/OFF strategy
> -The Radiant Slab Loop operates if the thermostat of the thermal zone requires it (ON/OFF strategy)
> -The heat pump works if the required temperature for the radiant slab loop isn't satisfied by the collector's energy gain. The temperature set for heating is 35 (°C) in the top of the storage tank. ON/OFF strategy
> 
> For some reason, when the heat pump is active its operating temperatures are above 60 (°C) at the heat pump's inlet, even if the tank is at 35 (°C). I've checked and the heat exchanger seems to transfer all the heat pump's energy to the storage tank. I don't know what is causing the temperature raise.
> 
> Is this what is supposed to happen? Is it a weird simulation unrealistic error?
> 
> My heat pump has a nominal capacityof 9 kW. The heat load transfered to the radiant slab is above 7 kW max. 
> 
> My heat pump's performance map has operating data just to 50 (°C) inlet water temperature. If I force the heat pump to work below this, the heat pump operates less often and the system can't supply enough energy to keep the radiant floor water at 35 (°C).
> 
> Here are two pics of the situation. First is the heat pump operating "naturally" at high temperature. Water inlet in the heat pump is in pink. Water temperature to the radiant slab is in blue. Heat output in the radiant slab is in green . Red is for the airnode temperature.
> 
> <image.png>
> 
> <image.png>
> 
> I would appreciate some help, thanks in advance.
> 
> King regards,
> Javier Vega
> 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170508/a3ae543c/attachment.htm>


More information about the TRNSYS-users mailing list